I thought the problem of the A/C fan starting on-off-on-off over & over was cured but it kept doing it. Turns out the new Silverleaf TM200 with firmware 1.39 that I acquired a few months ago has programming problems. I installed the original TM200 with firmware 1.16 & the A/C units are working correctly now.
The folks at Trillium are working on a new firmware to resolve the problem. The new TM200's have a different processer which requires programming changes & apparently I'm one of the guinea pigs.
The folks at Trillium are working on a new firmware to resolve the problem. The new TM200's have a different processer which requires programming changes & apparently I'm one of the guinea pigs.