Silverleaf Roof Air TM-200 Failure - No Compressor - Followed By No Heat TM-200
#6

I changed the thread title to add to the diagnostics after discovering that the Heat and the A/C controllers are somehow tied together.  My flawed logic of using Trillium Electronics tech support prior to calling Newell was based on the idea that they designed and manufactured it & should be the best source.  That did not work out.

After the A/C problem was cured by moving the TM-200's A/C Controller, I had Trillium Electronics program and ship a new #1 TM-200 A/C controller which I installed, all 4 A/C units worked great.  

On our next journey I discovered that I had no heat in zones that Silverleaf controlled, bedroom & kitchen.  Discussed with Silverleaf (Trillium Electronics) & sent the TM-220 Heat Controller to Trillium for testing.  They determined the TM-220 CPU failed and sold me a new TM-220.  Installed it, no change, returned it for reprogramming, reinstalled it, no change, no heat.  I foolishly did not ask for the original TM-220 with the "bad" CPU to be returned to me.

Called Newell, their electricians determined it to be a TM-200 A/C controller problem, NOT a TM-220 Heat Controller problem.  I removed the new #1 TM-200 A/C Controller & reinstalled the original #1 TM-200 A/C Controller & everything worked, heat and A/C.

I then sent all 3 TM-200 A/C Controllers to Newell to have the new #1 TM-200 programmed the same as the original #1 TM-200 and have them all tested in a coach of my vintage.  I installed them and with the new #1 TM-200 installed the kitchen heat works but the bedroom does not.  All 4 A/C units work.  I reinstalled the original #1 TM-200 & everything works, heat & A/C, but not correctly.  Now when I wake up, the Living Room heat is set to 74°, the room temperature was 67° but the blower will not blow until I move the temperature setting one degree, up or down, doesn't matter which way.  One morning the bedroom temperature setting had reverted to 38°.

I discovered that the A/C roof units Evaporator Water Pumps have a stainless steel shaft which makes them easily cleaned and lubed.  They are good quality.

To be continued.....

Jim
2014 Newell Coach 1482 Mid Entry 45'8" Valid Slides and Valid Levelling
Reply


Messages In This Thread
Silverleaf Roof Air TM-200 Failure - No Compressor - Followed By No Heat TM-200 - by hypoxia - 07-29-2025, 01:28 PM
RE: Silverleaf Roof Air TM-200 Failure - No Compressor - by Richard - 07-29-2025, 05:18 PM
RE: Silverleaf Roof Air TM-200 Failure - No Compressor - by CaptainGizmo - 07-30-2025, 02:53 PM
RE: Silverleaf Roof Air TM-200 Failure - No Compressor - by hypoxia - 07-30-2025, 04:15 PM
RE: Silverleaf Roof Air TM-200 Failure - No Compressor - by hypoxia - 07-31-2025, 01:43 PM