RE: SCS Capacitors - Richard - 07-12-2022

https://www.amazon.com/Coleman-83303362-Thermostat/dp/B004RCOU9Y/ref=asc_df_B004RCOU9Y/?tag=hyprod-20&linkCode=df0&hvadid=198099432697&hvpos=&hvnetw=g&hvrand=12483147605442744564&hvpone=&hvptwo=&hvqmt=&hvdev=t&hvdvcmdl=&hvlocint=&hvlocphy=1020899&hvtargid=pla-378949341804&psc=1

The only thing different from the orig Tstat is that this one will run both compressors until the setpoint is reached. The original will cut back to one compressor once the actual is within 2 degrees of setpoint.

Oh yeah, if you get that one, tie the two grey wires together. They are freeze protection circuit wires. If not tied together the compressors will not come on.